ER27-25: the filed comments

Positions read for this site

Each is a plain summary of one filing, checked against its pages. Where a stance is given, it is what the filing asks FERC to do with the proposal.

Two state commissions back the parallel study

Mississippi and Louisiana Public Service Commissions · Supports · ER27-25-000 · 2026-10-23

The commissions backed a 120-day joint study. They said studying the load and its generator together could avoid duplicating network upgrades; the limit of ten pairs per period made it manageable. They wanted a permanent process so projects could plan and finance construction.

The Southern Regulators support MISO’s filing to establish the LARS process and respectfully request that the Commission accept it. PDF p. 1

Arkansas signs on to the Southern regulators’ case

Arkansas Public Service Commission · Supports · ER27-25-000 · 2026-10-23

Arkansas expressly agreed with the Mississippi and Louisiana commissions’ comments and asked FERC to accept MISO’s tariff changes. It did not offer its own numerical estimate of costs or queue delays.

The APSC supports MISO’s filing to establish the LARS process, and agrees with the comments made by the Mississippi Public Service Commission and the Louisiana Public Service Commission. PDF p. 1

Consumer offices question the treatment of existing load

Iowa Office of Consumer Advocate, Illinois and Michigan attorneys general, Minnesota Department of Commerce and co-protesters · Opposes in part · ER27-25-000 · 2026-10-23

The joint protesters asked how the study would prevent costs shifting to other customers. They warned that related MISO proposals could exempt about 30 GW of existing load from some reliability requirements; 30 GW was not the size of the proposed LARS study queue.

the Joint Protestors pray the Commission reject MISO’s proposed Tariff grandfathering exemptions to ensure Large Load customers bear the cost and risk of all costs PDF p. 11

Google backs co-study but asks FERC to hold LARS until cost protections are filed

Google · Asks FERC to reject · ER27-25-000 · 2026-10-23

Google supported studying a load and its paired generation together, but said MISO filed LARS ahead of its cost-shifting protections. It asked FERC to reject LARS with guidance to refile alongside those protections or, in the alternative, accept and suspend it until they can be weighed together. It also wanted independent generators able to participate without discrimination by the serving utility.

the Commission should either reject LARS with guidance indicating that it needs to be filed concurrently with procedures to prevent cross-subsidization PDF p. 3

Bloom proposes 50 MW without delaying the filing

Bloom Energy · Supports with changes · ER27-25-000 · 2026-10-23

Bloom backed the study but challenged its 200 MW entry threshold. It proposed letting transmission-connected loads of at least 50 MW participate and asked FERC not to delay the requested start date.

LARS should therefore apply to loads of 50 MW or more that connect to the Transmission System. PDF p. 4

Who gets first claim on spare grid capacity?

American Clean Power Association and Southern Renewable Energy Association · Asks FERC to reject · ER27-25-000 · 2026-10-23

The trade associations said studying accelerated projects without other generators already waiting could leave later studies with fewer feasible connections and higher costs. They objected to a permanent parallel route without a cap on total capacity.

the Clean Energy Trades respectfully request that the Commission reject MISO’s LARS proposal. PDF p. 30

Solar developers challenge a utility veto

Solar Energy Industries Association and Advanced Energy United · Asks FERC to reject · ER27-25-000 · 2026-10-23

The protesters asked FERC to reject the proposal or clarify that an applicant meeting all published requirements could not lose access at the transmission customer’s discretion.

SEIA and United respectfully request that the Commission reject the LARS proposal, on the grounds that the proposal is unduly discriminatory PDF p. 2

A parallel queue can promise the same grid capacity twice

Clean Energy Advocates · Asks FERC to reject · ER27-25-000 · 2026-10-23

The advocates warned that two study tracks using different assumptions could count the same unused transmission capacity twice. They challenged assigning upgrade costs to existing customers based on agreements whose terms FERC had not seen.

For the reasons explained below, the Commission should reject the LARS proposal. PDF p. 1

Utilities say deposits and commitments screen speculative requests

Alliant Energy and Consumers Energy · Supports · ER27-25-000 · 2026-10-23

The utilities backed the readiness requirements because a speculative project could occupy one of a limited number of study slots. They argued the joint model could identify cheaper combined upgrades.

AECS and Consumers Energy respectfully request that the Commission accept the LARS Proposal. PDF p. 2

Entergy and Cleco contrast 120 days with years in the regular queue

Entergy and Cleco · Supports · ER27-25-000 · 2026-10-23

The utilities said some ordinary MISO study cycles had taken four years or more. They supported the 120-day path and argued that its cap of ten load-generator pairs per study period would keep it workable.

the Entergy Operating Companies and Cleco Power respectfully request that the Commission accept MISO’s LARS filing. PDF p. 6

DTE sees a binding match as evidence of readiness

DTE Electric · Supports · ER27-25-000 · 2026-10-23

DTE supported the pairing rules and minimum commitment as evidence of a lasting commercial relationship. It also said the tariff allowed the interconnection customer to participate even though the transmission customer submits the application.

DTE Electric supports the LARS filing and respectfully requests that the Commission accept the filing as proposed. PDF p. 2

MISO proposes parallel studies for paired load and generation

Midcontinent Independent System Operator · ER27-25-000 · 2026-10-02

MISO proposed LARS in a separate section 205 docket. It argued that modeling a matched pair could identify upgrades for the combination instead of each project separately. This was one proposed response to the June concerns. The full show cause case is still open.

MISO says independent generators can negotiate before applying

Midcontinent Independent System Operator · ER27-25-000 · 2026-11-09

MISO said the transmission customer submits an application for an already matched pair. It argued that an independent generator remains free to bring a proposal to that customer before the application, and that the eligibility rules are nondiscretionary.

MISO defends a higher entry threshold

Midcontinent Independent System Operator · ER27-25-000 · 2026-11-09

MISO defended 200 MW based on its experience with large-load studies. It said modeling the load and several associated plants together offered the largest potential savings where loads and upgrades were especially large.

NIPSCO backs LARS and cites 3,000 to 8,000 MW of inquiries

Northern Indiana Public Service Company · Supports · ER27-25-000 · 2026-10-22

NIPSCO asked FERC to accept MISO’s proposal effective December 2, 2026. It said it is considering requests to add between 3,000 and 8,000 MW of load, that the standard queue was not designed for paired load and generation, and that LARS would yield interconnection agreements in 120 days.

NIPSCO supports MISO’s LARS Proposal PDF p. 6

Base Electron supports LARS and asks MISO to confirm how the 150% cap is measured

Base Electron, Corp. · Supports · ER27-25-000 · 2026-10-23

Base Electron supported timely acceptance and did not ask FERC to delay or condition LARS. It asked for confirmation that the 150% limit on interconnection service is measured against the load’s full expected peak, including planned later phases, not its first phase.

Base Electron supports timely acceptance of MISO’s LARS Tariff proposal PDF p. 2

Transmission owners support LARS as an appropriately tailored tool

MISO Transmission Owners · Supports · ER27-25-000 · 2026-10-23

The transmission owners asked FERC to accept LARS effective December 2, 2026. They said it would yield an agreement in an estimated 120 days, is limited to three study cycles a year with ten applications per cycle, and keeps LARS requests out of the standard queue studies. The group lists Southern Minnesota Municipal Power Agency and NIPSCO among its members; both also filed separately, and SMMPA protested one part of LARS.

The MISO Transmission Owners support MISO’s LARS Filing PDF p. 4

Data center group backs LARS but wants independent generators to apply directly

Data Center Coalition · Supports with changes · ER27-25-000 · 2026-10-23

The coalition supported approving LARS but objected that every application must come through the load-serving entity, which keeps third-party generators from applying directly. It asked FERC to encourage MISO to let generators with demonstrated commercial pairings apply directly, or to add transparency on how utilities select applications.

DCC supports approval of the proposed LARS framework, but requests FERC encourage MISO to consider improvements for independent generator access PDF p. 7

Municipal utilities protest the zone-wide eligibility rule

Southern Minnesota Municipal Power Agency and WPPI Energy · Opposes in part · ER27-25-000 · 2026-10-23

The two municipal power suppliers protested one aspect of LARS, the rule that any generator and load in the same Local Resource Zone can pair. They said it departs from the Show Cause Order’s two-substation example and excludes close pairs in different zones. They asked FERC to reject that scope and to condition acceptance on a later finding that MISO addressed cost allocation and transparency.

MISO’s Filing does not come close to justifying a departing from the Show Cause Order’s approach by substituting a geographic scope that is both overinclusive and underinclusive PDF p. 5

Geronimo says utility gatekeeping makes LARS unduly discriminatory

Geronimo Power · Asks FERC to reject · ER27-25-000 · 2026-10-23

Geronimo supported coordinated study in principle but said a generator cannot enter LARS without the transmission owner’s sign-off on its point of interconnection and a utility sponsor for the application. It also said MISO’s wording could exclude generators selling under virtual power purchase agreements and co-located generation and load. It asked FERC to reject LARS without prejudice to a revised filing.

Geronimo Power urges the Commission to reject LARS on the basis that it has not been shown to be just, reasonable, and not unduly discriminatory or preferential PDF p. 5

Invenergy asks that merchant DC lines be eligible for LARS

Invenergy Transmission · Supports with changes · ER27-25-000 · 2026-10-23

Invenergy said LARS fits FERC and DOE goals but that its definitions appear to admit only generating facilities. It asked FERC to direct MISO, on compliance, to clarify that merchant high voltage direct current lines and generation connected to them can participate, and attached a tariff redline.

Invenergy therefore respectfully requests that the Commission direct MISO, on compliance, to revise the proposed Tariff to clarify that MHVDC transmission lines are eligible to participate in the LARS process PDF p. 5

Geronimo says MISO’s answer leaves the discrimination concerns unaddressed

Geronimo Power · Asks FERC to reject · ER27-25-000 · 2026-11-18

Geronimo said MISO’s answer gave only a generic response on virtual power purchase agreements and did not address co-location and did not justify the roles of load-serving entities and transmission owners. It said a transmission owner could also remove a project by changing the point of interconnection. It again asked FERC to reject LARS without prejudice to a revised filing.

Geronimo Power urges the Commission to reject LARS without prejudice to MISO submitting a revised proposal that addresses the significant issues identified by Geronimo Power and other parties in this proceeding PDF p. 2

Municipal utilities say MISO’s answer does not justify the zone-wide scope

Southern Minnesota Municipal Power Agency and WPPI Energy · Opposes in part · ER27-25-000 · 2026-11-19

Answering MISO’s November 9 answer, the two suppliers said MISO’s “maximum flexibility” rationale does not show the zonal scope meets the Show Cause Order. They said cost-shifting protections rest on MISO’s separate Nov 16 filings, not the LARS tariff, and repeated that FERC should reject the geographic scope and condition acceptance rather than delay LARS.

the inclusion in LARS of pairs of generation and load that do not reduce the need for Network Upgrades (e.g., those not electrically proximate) risks crowding out those pairs that do create greater efficiencies PDF p. 7

Other passages, matched by topic

These passages match a topic and a request or argument in the same sentence. A filing can quote another party. Read its page before attributing a position.

Connecting load and generation

MISO

ER27-25-000 · 2026-11-09

4 Also, because a number of commenters misstate the intent and background of LARS, raise extraneous issues, seek clarifications, and/or propose changes, MISO requests permission to respond to the intervenors’ arguments to clarify the record and assist the Commission with its decision-making. PDF p. 2

Arkansas PSC

ER27-25-000 · 2026-10-23

The APSC supports MISO’s filing to establish the LARS process, and agrees with the comments made by the Mississippi Public Service Commission and the Louisiana Public Service Commission. Source text

DTE Electric

ER27-25-000 · 2026-10-23

1 DTE Electric supports MISO's proposal and believes the LARS framework represents a reasonable approach to evaluating the transmission, operational, and resource adequacy impacts associated with significant new load additions and associated generation resources within the MISO footprint. PDF p. 1

Entergy and Cleco

ER27-25-000 · 2026-10-23

Entergy and Cleco Power LLC support MISO’s October 2, 2026, filing to establish the LARS process, and respectfully urges the Commission to accept it, as it will enable MISO to expeditiously review the interconnection needs of large loads over 200 MW that have identified new generation resources to support their needs. PDF p. 1

Mississippi and Louisiana PSCs

ER27-25-000 · 2026-10-23

The Southern Regulators support MISO’s filing to establish the LARS process and respectfully request that the Commission accept it. PDF p. 1

ACP and SREA

ER27-25-000 · 2026-10-23

2 members include independent power producers (“IPPs”) that develop generation to serve large loads and that would be directly affected by both the access rules LARS establishes and the effect of LARS on the transmission capacity and Network Upgrade costs available to projects in the DPP. PDF p. 2

Bloom Energy

ER27-25-000 · 2026-10-23

Bloom supports LARS and urges the Commission to accept it by MISO's requested December 2, 2026 effective date. PDF p. 1

Iowa OCA and 8 consumer advocates

ER27-25-000 · 2026-10-23

Cost-Shifting Should be Addressed Across MISO’s Section 205 Filings and in the Section 206 Filing MISO’s LARS Process does not address the Commission’s concerns regarding cost- shifting expressed in the Show Cause Order. PDF p. 4

Google

ER27-25-000 · 2026-10-23

3 The concept underlying LARS is a particularly important one that is worth prioritizing, and it is a concept that Google continues to strongly support. PDF p. 1

Base Electron, Corp.

ER27-25-000 · 2026-10-23

Base Electron supports the initiatives undertaken by MISO to develop LARS and implement it in its Tariff. PDF p. 1

MISO Transmission Owners

ER27-25-000 · 2026-10-23

3 As detailed in the LARS Filing, the LARS process provides a streamlined and flexible process whereby MISO is able to expedite the study of load interconnection requests of 200 megawatts (“MW”) or greater that are paired with electrically proximate new generation resources. PDF p. 2

Individual No Affiliation

ER27-25-000 · 2026-10-23

Their relevance here is methodological: MISO should explain how LARS preserves consistent cumulative assumptions across EPR, DPP, and MTEP, distinguishes existing or generation-driven facilities from incremental large-load-driven costs, and retains the evidence needed to attribute later upgrades appropriately. PDF p. 5

Data Center Coalition

ER27-25-000 · 2026-10-23

By evaluating this group of load and generation pairs on a coordinated and concurrent basis, LARS offers a practical tool that will bring essential supply online quickly to support MISO’s economic growth while optimizing network upgrades and protecting overall customer affordability. PDF p. 3

GERONIMO POWER, LLC

ER27-25-000 · 2026-10-23

As currently conceived, LARS would provide incumbent utilities with undue influence over the ability of interconnection customers to access the process. PDF p. 3

Invenergy Transmission LLC

ER27-25-000 · 2026-10-23

3 For the reasons set forth below, Invenergy respectfully requests that the Commission direct MISO to clarify that Merchant High Voltage Direct Current (“MHVDC”) facilities and generating facilities interconnected to MHVDC are eligible to participate in LARS, thereby ensuring entities capable of providing capacity to large load customers seeking interconnection to the MISO system are able to do so through the LARS process. PDF p. 1

Cost allocation

MISO

ER27-25-000 · 2026-11-09

13 LARS Helps Mitigate Cost Shifting, Supports Cost Causation Principles, and Addresses Urgent Needs Now Without Prejudicing Subsequent Large Load Reforms Second, MISO recognizes the importance of developing a cost allocation framework that will prevent cost shifting and align with the Commission’s cost causation principles. PDF p. 4

ACP and SREA

ER27-25-000 · 2026-10-23

2 members include independent power producers (“IPPs”) that develop generation to serve large loads and that would be directly affected by both the access rules LARS establishes and the effect of LARS on the transmission capacity and Network Upgrade costs available to projects in the DPP. PDF p. 2

Iowa OCA and 8 consumer advocates

ER27-25-000 · 2026-10-23

Consistent with the Show Cause Order, the cost-causer, not other ratepayers, should be responsible for all network upgrades resulting from the Large Load. PDF p. 7

Google

ER27-25-000 · 2026-10-23

To be clear, Google supports both the concept underlying LARS, which will improve speed to power and transmission planning, and provisions that protect other network customers against cost shifting. PDF p. 3

Individual No Affiliation

ER27-25-000 · 2026-10-23

Such information would allow regulators and transmission customers to examine both legitimate shared benefits and potential unjustified cost shifting. PDF p. 3

Data Center Coalition

ER27-25-000 · 2026-10-23

DCC advocates for grid reforms that minimize unnecessary cost burdens, align with cost causation principles, facilitate responsible load growth, support the development of new generation, and enhance grid resilience system-wide without imposing undue costs on existing ratepayers. PDF p. 2

GERONIMO POWER, LLC

ER27-25-000 · 2026-10-23

At the same time, certain aspects of MISO’s proposed framework appear to arbitrarily exclude from LARS generation resources that are being developed to meet the demand of large load customers in a manner that supports resource adequacy and protects ratepayers. PDF p. 3

Filing procedure

ACP and SREA

ER27-25-000 · 2026-10-23

4 (2026) (“ERAS Rehearing Order”) (noting rehearing request of the Clean Energy Associations, including ACP). PDF p. 2

Registry access

MISO

ER27-25-000 · 2026-11-09

In developing LARS, MISO concluded that defining a maximum distance based on substations would impede the flexibility of large loads and 19 Clean Energy Trades LARS Comments at 18; the Community Organizations and Clean Energy Advocates (the “Advocates”) LARS Comments at 37-38; Consumer Advocates LARS Comments at 9; OMS LARS Comments at 8; and the Southern Minnesota Municipal Power Agency and WPPI Energy (the “Midwest TDUs”) LARS Comments at 5-6. PDF p. 9

Reliability and curtailment

MISO

ER27-25-000 · 2026-11-09

13 LARS Heeds the Call for Speed to Power and Supports Resource Adequacy The immensity and rate of large load additions across the United States is requiring unique proposals. PDF p. 13

DTE Electric

ER27-25-000 · 2026-10-23

1 DTE Electric supports MISO's proposal and believes the LARS framework represents a reasonable approach to evaluating the transmission, operational, and resource adequacy impacts associated with significant new load additions and associated generation resources within the MISO footprint. PDF p. 1

MISO Transmission Owners

ER27-25-000 · 2026-10-23

2026) (projecting annual load growth of approximately 1% to 2% through 2044 and identifying data centers, manufacturing expansion, and electrification as drivers of sustained, concentrated load growth); see also, MISO, 2026 Planning Resource Auction Results at 2 (May 22, 2026) (stating that faster resource additions are needed to support large-load growth and ensure resource adequacy)). PDF p. 6

GERONIMO POWER, LLC

ER27-25-000 · 2026-10-23

At the same time, certain aspects of MISO’s proposed framework appear to arbitrarily exclude from LARS generation resources that are being developed to meet the demand of large load customers in a manner that supports resource adequacy and protects ratepayers. PDF p. 3

Invenergy Transmission LLC

ER27-25-000 · 2026-10-23

There is no reason to exclude such resources if they are capable of satisfying all other applicable eligibility requirements of the LARS process, and their inclusion would meaningfully advance MISO’s ability to maintain resource adequacy across the region. PDF p. 5

Retail and wholesale authority

ACP and SREA

ER27-25-000 · 2026-10-23

While it is reasonable for LSEs to initiate and oversee LARS requests on the load side, given state jurisdiction over retail service and LSEs’ obligations to serve load, that logic does not 36 See Order No. PDF p. 10