ER26-1479: the filed comments

These passages match a topic and a request or argument in the same sentence. A filing can quote another party. Read its page before attributing a position.

Connecting load and generation

Digital Power Network

ER26-1479-000 · 2026-03-16

The Commission should ensure that PJM’s new co-located load transmission service framework preserves the operational flexibility of flexible loads. PDF p. 3

EDF Power Solutions, Inc.

ER26-1479-000 · 2026-03-16

This would force new generation resources – which are solely intended to serve new large loads – into the generation interconnection queue with full wholesale interconnection studies that would otherwise be unnecessary. PDF p. 4

Advanced Energy UnitedSolar Energy Industries Association

ER26-1479-000 · 2026-03-16

The temporary closure of PJM’s interconnection queue to new generation,12 significant 12 PJM effectively closed its interconnection process to new applicants in 2022 and expects to initiate the first cluster study of new requests in April 2026. PDF p. 5

PJMICC, IECA, AF&PA, and Amtrak

ER26-1479-000 · 2026-03-16

It is important to note that providing legacy retail behind-the-meter generation netting treatment for all Qualifying Facilities would not provide a “back door” for very large computational loads to bypass the Co-Located Load provisions of FERC’s December 18, 2025, Show Cause Order in Docket No. PDF p. 74

Vistra Corp.

ER26-1479-000 · 2026-03-16

26 PJM would require existing generators that seek to add co-located load to submit to PJM “the amount of reduction to Capacity 22 Press Release, Dep’t of Energy, Energy Department Launches Speed to Power Initiative, Accelerating Large- Scale Grid Infrastructure Projects (Sept. PDF p. 8

Constellation Energy Generation, LLC

ER26-1479-000 · 2026-03-16

Even if such claims might eventually be overturned by the Commission, changing the definition of Co-Located Load would allow Transmission Owners to use the determination of the Point of Change in Ownership to cause unnecessary delay or other mischief for large load projects seeking speed to service from competitive suppliers. PDF p. 5

American Municipal Power, Inc.

ER26-1479-000 · 2026-03-16

PJM’s proposed definition of Non-Retail BTMG should be rejected because it is unnecessary and could exclude otherwise eligible generation facilities from Co-Located Load configurations. PDF p. 4

Maryland Office of People's Counsel

ER26-1479-000 · 2026-03-16

If the capacity of existing generation that shifts to serve new co-located data center load is added to the BRA, ratepayers would be saddled with enormous costs that should be assigned to the co-located load, in contravention of the Statement of Principles and the Ratepayer Protection Pledge. PDF p. 10

Crusoe Energy Systems, Inc.

ER26-1479-000 · 2026-03-16

The Commission should direct PJM to revise the threshold upward and calibrate it to the size of the co-located load at the relevant electrical location. PDF p. 2

Constellation Energy Generation, LLC

ER26-1479-000 · 2026-04-08

While such load would still be Co-located Load under the December 18th Order’s definition—it is still on the generator’s side of the Point of Interconnection, notwithstanding the Transmission Owner’s ownership of facilities on that side— it would no longer count as Co-located Load under PJM’s alternative definition focused on the Point of Change in Ownership. PDF p. 2

Exelon Corporation

ER26-1479-000 · 2026-04-14

Nonetheless, Constellation argues that this interaction demonstrates the inadequacy of PJM’s proposed definition of co-located load. PDF p. 3

Indicated PJM Transmission Owners

ER26-1479-000 · 2026-04-24

It is unclear what Invenergy is asking for here, but to the extent it is requesting that the Commission impose a combined transmission and interconnection study process for Co-Located Load and generation, the Commission should decline. PDF p. 5

Vistra Corp.

ER26-1479-001 · 2026-07-20

Vistra expressed concern that the tariff could be read to require generators to delist CIRs associated with any facility that would ever provide power to Co-Located Load, not just the portion of the facility designated to serve the Co-Located Load. PDF p. 4

Exelon CorporationThe FirstEnergy Transmission Companies

ER26-1479-001 · 2026-07-20

The June 18, 2026 Order addressed rehearing requests relating to the Commission’s December 18, 2025 Order6 in this proceeding, concerning the Commission’s determination that the existing Network Service in the PJM Tariff is unjust and unreasonable for service to Co- Located Load and requiring that three new forms of service be made available for Co-Located Load: Firm Contract Demand Network Service (“FCD”); Non-Firm Contract Demand Network Service (“NFCD”); and Interim Network Service. PDF p. 2

Constellation Energy Generation, LLC

ER26-1479-001 · 2026-07-20

3 In addition, Constellation seeks clarification, or in the alternative, rehearing on the Commission’s denial of Constellation’s request to modify the definition of Co-Located Load Generating Facility so that only the portion of the Generating Facility serving the Co-Located Load be considered the Co-Located Generating Facility. PDF p. 3

Eolian, L.P.Calibrant EnergyVerrus LLC ,

ER26-1479-001 · 2026-07-20

26 However, clarification is needed to confirm that all resources not obligated to deliver to PJM or another entity are eligible to support Interim NITS customers, because the Commission explicitly requires tariff modification only with regard to the specific circumstances it discusses27—leaving out additional circumstances for which a co-located resource could provide capacity to its co-located load without being a Generation Capacity Resource. PDF p. 13

Indicated PJM Transmission Owners

ER26-1479-001 · 2026-07-20

4 As discussed below, the Commission should grant rehearing or provide clarification of the June 18 Order, as follows:  The Commission erred in concluding that co-located load and generation interconnected and synchronized with the transmission system should be exempt from any minimum charge, such as the Grid Reliance Charge proposed by the PJM Transmission Owners. PDF p. 2

PJMICC, IECA, AF&PA, and Amtrak

ER26-1479-000 · 2026-09-08

The term Co-Located Load, at least in some cases, could be interpreted as applying to Retail BTMG facilities as well—particularly in the situations (1) where the Retail BTMG is a QF that makes wholesale sales of excess generation, or (2) where there are commercial arrangements that otherwise would qualify for grandfathering. PDF p. 6

Cost allocation

PJMICC, IECA, AF&PA, and Amtrak

ER26-1479-000 · 2026-03-16

It is also important to note the retail behind the meter generation netting approach would work under different cost allocation methods besides the annual coincident peak demand method. PDF p. 64

Vistra Corp.

ER26-1479-000 · 2026-03-16

A broad reading that would require units that provide only occasional, interruptible energy to co- located load to delist their CIRs would deprive ratepayers of generation that is generally available to serve the grid when needed and risk unnecessarily increasing capacity prices. PDF p. 10

Calibrant EnergyAntora Energy LLCEolian, L.P. ,Convergent Energy and Power LP ,Mainspring Energy ,

ER26-1479-000 · 2026-03-16

Such a nameplate generation-based threshold is also unjust and unreasonable and unduly discriminatory because it would also unnecessarily constrain commercial opportunities to serve loads with BTMG without better protecting reliability or commensurate reductions in resource adequacy or cost shift risks and treat differently BTMGs with similar resource adequacy and cost shift impacts. PDF p. 2

Maryland Office of People's Counsel

ER26-1479-000 · 2026-03-16

Thus, the thrust of the Statement of Principles and the Ratepayer Protection Pledge is that generally new data centers should pay for new capacity. PDF p. 9

Crusoe Energy Systems, Inc.

ER26-1479-000 · 2026-03-16

Crusoe supports policy efforts that facilitate “bring your own power” frameworks and are built on an energy- first model that allow co-located generation to enhance grid reliability, reduce ratepayer costs, and accelerate the buildout of AI infrastructure. PDF p. 1

PJMICC, et al.

ER26-1479-001 · 2026-07-20

The Industrials/Amtrak respectfully request that the Commission adopt a 200 MW Retail Threshold and a broad exemption for QFs to preserve the investment environment in American manufacturing in the PJM region, consistent with cost causation principles and Commission Regulations. PDF p. 14

Filing procedure

Energy Artisans, LLC

ER26-1479-000 · 2026-03-16

As established in the PJM ICC Request for Rehearing/Clarification in Docket EL25-49, filed on January 20, 2026, and supported by the C&I clients we represent and our direct experience, the 200 MW threshold is a far more practical solution for existing industrial and institutional loads that have long relied on their on-site investments to manage electric and other commodity costs efficiently. PDF p. 2

PJMICC, IECA, AF&PA, and Amtrak

ER26-1479-000 · 2026-03-16

Unlike the surge in large-load demands from data centers and computational workloads, most manufacturers are simply trying to survive and keep their facilities 8 PJMICC and IECA (together, “Requestors”) jointly filed a Request For Clarification or, in the Alternative, Rehearing of the Industrial Customer Coalitions (“Rehearing Request”) on January 20, 2026, in Docket No. PDF p. 3

Vistra Corp.

ER26-1479-000 · 2026-03-16

, Constellation Request for Clarification or, in the Alternative, Rehearing, Docket Nos. PDF p. 10

Vistra Corp.

ER26-1479-001 · 2026-07-20

ER26-1479-000 REQUEST FOR CLARIFICATION OR, IN THE ALTERNATIVE, REHEARING OF VISTRA CORP. PDF p. 1

Exelon CorporationThe FirstEnergy Transmission Companies

ER26-1479-001 · 2026-07-20

, Delmarva Power & Light Company, PECO Energy Company, and Potomac Electric Power Company 4 FirstEnergy Service Company submits this rehearing request as agent for its affiliates American Transmission Systems, Incorporated, Jersey Central Power & Light Company, Mid-Atlantic Interstate Transmission LLC, Keystone Appalachian Transmission Company, The Potomac Edison Company, Monongahela Power Company and Trans-Allegheny Interstate Line Company (collectively, the “FirstEnergy Transmission Companies”). PDF p. 1

Constellation Energy Generation, LLC

ER26-1479-001 · 2026-07-20

3 In addition, Constellation seeks clarification, or in the alternative, rehearing on the Commission’s denial of Constellation’s request to modify the definition of Co-Located Load Generating Facility so that only the portion of the Generating Facility serving the Co-Located Load be considered the Co-Located Generating Facility. PDF p. 3

Eolian, L.P.Calibrant EnergyVerrus LLC ,

ER26-1479-001 · 2026-07-20

(“Eolian”), Calibrant Energy Holdings, LLC (“Calibrant”), and Verrus, LLC request clarification, and the in alterative rehearing of the Commission’s June 18 Order in the above-captioned proceeding (Order). PDF p. 1

PJMICC, et al.

ER26-1479-001 · 2026-07-20

2 The Industrials/Amtrak respectfully ask the Commission to 1) establish a retail Behind the Meter Generation (“BTMG”) netting threshold of 200 Megawatts (“MW”); and 2) grant their rehearing requests regarding Qualifying Facilities (“QFs”) under the Public Utility Regulatory Policies Act of 1978 (“PURPA”), including a QF’s right to be served with just and reasonable back-up and maintenance power. PDF p. 1

PJMICC, IECA, AF&PA, and Amtrak

ER26-1479-000 · 2026-09-08

Amtrak consumes substantial 6 On January 20, 2026, PJMICC and IECA jointly filed a Request For Clarification or, in the Alternative, Rehearing of the Industrial Customer Coalitions (“December Order Rehearing Request”), in Docket No. PDF p. 3

Registry access

Exelon Corporation

ER26-1479-000 · 2026-04-14

112 of the Commission’s regulations,3 Exelon requests privileged treatment for a portion of this Answer containing certain confidential information. PDF p. 2

Reliability and curtailment

Digital Power Network

ER26-1479-000 · 2026-03-16

12 DPN is concerned that, absent further clarification, those requirements and the structure of the new service pathways could reduce the incentives for flexible load projects to preserve curtailment-capable operating models that benefit the grid. PDF p. 3

EDF Power Solutions, Inc.

ER26-1479-000 · 2026-03-16

Large loads electing to take “Interim NITS” accept the risk of grid curtailment but they should not have to accept a complete operational downtime during a grid curtailment. PDF p. 8

Advanced Energy UnitedSolar Energy Industries Association

ER26-1479-000 · 2026-03-16

This has placed significant stress on the region’s ability to meet its resource adequacy requirements, at a time when the interconnection of new generation has been stalled as PJM works through a backlog of requests and implements new reforms. PDF p. 2

PJMICC, IECA, AF&PA, and Amtrak

ER26-1479-000 · 2026-03-16

42 Consequently, the FERC’s path forward to implement the Order should consider the performance of these units and the substantial resource adequacy contributions of BTMG, including in developing a reasonable Retail Threshold. PDF p. 16

Data Center Coalition

ER26-1479-000 · 2026-03-16

”6 This is unworkable because curtailment should limit use of the grid, not prevent the customer from using the co-located resource it supplied, which supports Interim NITS in the first place. PDF p. 6

Vistra Corp.

ER26-1479-000 · 2026-03-16

And where the Commission required pragmatism, PJM has responded with a truly byzantine proposal for Capacity Interconnection Rights (“CIRs”) that is clear as mud and appears likely to limit backup resources’ ability to support resource adequacy where they can. PDF p. 2

Appalachian Voices

ER26-1479-000 · 2026-03-16

5 would unjustly and unreasonably shift costs and exacerbate the reliability and resource adequacy risks the Commission has already identified. PDF p. 5

Calibrant EnergyAntora Energy LLCEolian, L.P. ,Convergent Energy and Power LP ,Mainspring Energy ,

ER26-1479-000 · 2026-03-16

Such a nameplate generation-based threshold is also unjust and unreasonable and unduly discriminatory because it would also unnecessarily constrain commercial opportunities to serve loads with BTMG without better protecting reliability or commensurate reductions in resource adequacy or cost shift risks and treat differently BTMGs with similar resource adequacy and cost shift impacts. PDF p. 2

Constellation Energy Generation, LLC

ER26-1479-000 · 2026-03-16

, 192 FERC ¶ 61,135, at P 21 (2025) (the Commission’s analysis of whether a PJM proposal would be just and reasonable to count certain Reliability Must-Run (“RMR”) resources in the capacity market—despite the RMR units not being “a perfect substitute” for capacity—focused on “whether PJM can commit an RMR resource during emergency conditions to help meet the system’s resource adequacy needs”). PDF p. 20

Maryland Office of People's Counsel

ER26-1479-000 · 2026-03-16

Regarding protecting residential customers, the Statement of Principles states that due to data centers’ size and risks they pose to resource adequacy, “PJM should allocate the cost of any new capacity procured through the aforementioned Reliability Backstop Auction to load serving entities (LSEs) with new data centers that have not self-procured new capacity or agreed to be curtailable. PDF p. 3

Crusoe Energy Systems, Inc.

ER26-1479-000 · 2026-03-16

Second, while PJM’s Interim Network Integration Transmission Service (Interim NITS) is a useful tool to help facilitate large load interconnections, it should be clarified to ensure that co-located generation is able to supply co-located load during curtailment events, including while the generator is still being studied in the interconnection process. PDF p. 2

Indicated PJM Transmission Owners

ER26-1479-000 · 2026-04-24

The Order expressly directed PJM to propose a new MW threshold for Retail BTMG and explained that such a threshold should reduce the reliability and resource adequacy 3 See PJM 60-Day Compliance Filing, Docket No. PDF p. 2

Vistra Corp.

ER26-1479-001 · 2026-07-20

Doing so would deprive the generation resource owner of its ability to provide capacity to PJM—and harm resource adequacy in PJM—for no conceivable reason, resulting in unjust and unreasonable rates. PDF p. 17

Constellation Energy Generation, LLC

ER26-1479-001 · 2026-07-20

37 If disqualification after the first failure to follow a load shed or curtailment directive is “unnecessarily strict,” so too should a four-month disqualification for the misoperation of control technologies and/or protection systems that may be unrelated to actions taken by the load or Eligible Customer. PDF p. 12

Eolian, L.P.Calibrant EnergyVerrus LLC ,

ER26-1479-001 · 2026-07-20

First, the Commission should clarify that PJM's tariff must generally describe the reliability principles and circumstances under which these services may be curtailed, and not merely their relative curtailment priority. PDF p. 1

PJMICC, et al.

ER26-1479-001 · 2026-07-20

16 June Order at P 246 (“certain cogeneration QFs should be exempted from the replacement rate upon a demonstration that they do not present the reliability or resource adequacy concerns discussed in the December Order”); see also id. PDF p. 5

Retail and wholesale authority

Exelon Corporation

ER26-1479-000 · 2026-04-14

Because these are studies of service requests for new end users, aspects of their conduct and their application to those retail service applications are subject to regulation by state utility commissions. PDF p. 11