Positions read for this site
Each is a plain summary of one filing, checked against its pages. Where a stance is given, it is what the filing asks FERC to do with the proposal.
Office of the Ohio Consumers’ Counsel · ER26-3515-001 · 2026-11-09
Ohio’s consumer advocate asked FERC to give state consumer offices the same confidential access available to commissions. Customers need an advocate who can test costs and curtailment decisions, it argued. Its November 9 request challenges the October order. It does not ask PJM to publish customer records.
Office of the Ohio Consumers’ Counsel · ER26-3515-001 · 2026-11-09
OCC sought rehearing of the October 9 order. It asked FERC to reject the registry unless PJM grants consumer advocates access under confidentiality agreements.
Pennsylvania Public Utility Commission · ER26-3515-000 · 2026-09-03
Pennsylvania’s commission supported creating a registry but wanted state commissions to have access and wanted PJM to record curtailments. Its comments addressed the proposal before FERC rejected interim curtailment service.
Pennsylvania Public Utility Commission · ER26-3515-000 · 2026-09-03
Pennsylvania’s commission supported creating a registry but wanted state commissions to have access and wanted PJM to record curtailments. Its comments addressed the proposal before FERC rejected interim curtailment service.
Data Center Coalition · ER26-3515-000 · 2026-09-03
The coalition supported letting customers bring their own generation but opposed the proposed interim service. It argued that PJM’s region-wide mandatory curtailment rule would displace state retail decisions.
Joint Consumer Advocates · ER26-3515-000 · 2026-09-03
The advocates saw value in a choice between contributing new capacity and curtailing with appropriate state action. With suitable eligibility rules, they argued, this mechanism would make a separate backstop procurement redundant.
These passages match a topic and a request or argument in the same sentence. A filing can quote another party. Read its page before attributing a position.
Cost allocation
ER26-3515-000 · 2026-09-03
Instead, as it is currently set forth in the proposed tariff, adoption of PJM’s curtailment compensation proposal would impede states’ ability to enforce any NLL’s commitment to protect ratepayers from the costs that the NLL is causing. PDF p. 6
ER26-3515-000 · 2026-09-03
This mechanism will protect ratepayers from bearing capacity costs that should rightfully be borne by new large loads or otherwise bearing excessive and unnecessary capacity costs associated with phantom load projections. PDF p. 10
ER26-3515-000 · 2026-09-03
PJM asks the Commission to accept a wholesale rate that has no value and a cost allocation that has no allocator. PDF p. 1
ER26-3515-000 · 2026-09-03
And although clarification of this issue is important to protecting everyday ratepayers, it is permissible because it would not result in an entirely different rate design than what 14 For example, PJM should consider clarifying that the Electric Distributor would fulfill the IRAS Action by dropping the New Large Load to zero if the total IRAS Action MW directive exceeds the actual amount of New Large Load online in real-time. PDF p. 7
ER26-3515-000 · 2026-09-03
” The PSCWV does not fully support PJM’s structure to address unusual and historic capacity needs created by growth in NLL, mostly associated with the growth of data centers, however, it does agree with the goals enumerated in the Administration’s Ratepayer Protection Pledge and similar ratepayer protections plans put forth by the Governors of the thirteen PJM States. PDF p. 2
ER26-3515-000 · 2026-09-03
Cost Causation Principles Support a Zero-Dollar Rate or a Capacity-Charge Credit. PDF p. 4
ER26-3515-000 · 2026-09-03
Likewise, limiting PSA eligibility to participants in the RBP would limit the benefits of large- load funded PSA-eligible load reduction programs to only a subset of large load coming online in the near future, rather than establishing a more permanent pathway for large load customers to fund demand-side programs that can reduce zonal capacity obligations and provide immediate ratepayer benefits. PDF p. 5
ER26-3515-000 · 2026-09-03
This treatment will help protect ratepayers from capacity market cost increases that would have been caused by future large loads. PDF p. 4
ER26-3515-000 · 2026-09-03
Given the enthusiasm with which many large load developers and Electric Distributors have signed the Ratepayer Protection Pledge,10 there should clearly be a high level of interest in voluntarily participating in such a program. PDF p. 3
ER26-3515-000 · 2026-09-03
Should PJM fail to prioritize IRAS Actions, such as re-sequence them to occur just prior to the issuance of manual load shed under an EEA3, damage to retail ratepayers will already have been done. PDF p. 7
ER26-3515-000 · 2026-09-03
This should also apply to reduction in Reliability Backstop Procurement (RBP) cost allocations, with large loads that secure verified demand reductions (such as through the Peak Shaving Adjustment) being appropriately credited for their reduction in impacts on the grid. PDF p. 3
ER26-3515-000 · 2026-09-03
”217 PJM contends that including Eligible New Large Load in the demand curve “would fail to recognize that New Large Loads have committed to ‘build, bring, or buy the new generation resources and electricity needed to satisfy their new energy demands,’” which PJM asserts is consistent with the Ratepayer Protection Pledge. PDF p. 48
ER26-3515-000 · 2026-09-03
The Ratepayer Protection Pledge, however, is not a binding legal document and would not prevent new large loads from seeking compensation pursuant to the IRAS Proposal mechanisms. PDF p. 5
ER26-3515-000 · 2026-09-03
, 155 FERC ¶ 61,076, at P 82 (2016) (rejecting proposal that would have required ratepayers to pay twice for the same capacity). PDF p. 17
ER26-3515-000 · 2026-09-03
Accordingly, even if the Ratepayer Protection Pledge could be reimagined as supporting PJM’s IRAS proposal, the Commission would still be statutorily bound to reject that proposal. PDF p. 10
ER26-3515-000 · 2026-09-03
The filing does not explain why, absent such a waiver or alternative retail treatment, other customers should fund these payments or how that outcome is consistent with principles of cost causation and the stated objective of protecting existing ratepayers from costs associated with New Large Load growth. PDF p. 61
ER26-3515-000 · 2026-09-03
Fourth, IRAS participants should not receive compensation that shifts costs to other ratepayers. PDF p. 4
ER26-3515-000 · 2026-09-03
RETAIL COST ALLOCATION AND STATE COORDINATION As stated above, United supports the goal of IRAS: to incentivize new large loads to bring their own new capacity, and to ensure that those that do not, and that thus contribute to the 14 Proposed Tariff, Attachment DD-4, § VI(b)(i)(3); Transmittal Letter at 54. PDF p. 9
ER26-3515-000 · 2026-09-03
21 PJM argued that removing such New Large Loads is consistent with the Ratepayers Protection Pledge and would lower capacity market clearing prices for PJM customers. PDF p. 11
ER26-3515-000 · 2026-09-04
OPSI SUPPORTS THE LARGE LOAD REGISTRY TO INFORM RETAIL CURTAILMENT AND COST ALLOCATION OPSI supports PJM’s proposed Large Load Registry because it will provide states and Electric Distributors with the information needed to design and administer retail curtailment and cost-allocation mechanisms for NLLs. PDF p. 7
Registry access
ER26-3515-000 · 2026-09-03
1 PA PUC supports the creation and maintenance of a New Large Load (NLL) Registry and suggests improvements to the Registry. PDF p. 2
ER26-3515-000 · 2026-09-03
In addition, the Commission should direct modification of the proposal to require its review and validation of data supplied for the Large Load Registry, and to expand access to the information in the Registry such that the JCA can review the data. PDF p. 2
ER26-3515-000 · 2026-09-02
The Large Load Registry and associated implementation processes should therefore preserve sufficient provenance to allow authorized users to distinguish among: represented capability; capability supported by implementation evidence; actual observed performance; and the quantity ultimately used for compensation. PDF p. 4
ER26-3515-000 · 2026-09-03
I support approval of the Interim Resource Adequacy Service (IRAS), the Large Load Registry, and the Bring Your Own New Capacity (BYONC) provisions. PDF p. 1
ER26-3515-000 · 2026-09-03
PJM would maintain that information in the Large Load Registry and rely on States and Electric Distributors to act on it. PDF p. 13
ER26-3515-000 · 2026-09-03
Nonetheless, PJM should consider clarifying that if Electric Distributors, in coordination with these entities, do not take action, PJM will use the registry to curtail New Large Loads ahead of all other loads. PDF p. 5
ER26-3515-000 · 2026-09-03
In rejecting the filing, the Commission should encourage PJM to refile the Large Load Registry proposal as a separate Section 205 submission while offering to provide all necessary and appropriate support to state commissions seeking to integrate large loads at the distribution level on terms and conditions set by state regulatory authority. PDF p. 46
ER26-3515-000 · 2026-09-03
The Commission should accept PJM’s Interim Resource Adequacy Service and Large Load Registry with modifications to better achieve the IRAS’s objectives. PDF p. 3
ER26-3515-000 · 2026-09-03
Large Load Registry The Board supports the proposed Large Load Registry and appreciates PJM’s role in leading the development and maintenance of such registry. PDF p. 13
ER26-3515-000 · 2026-09-03
FERC should direct PJM to modify the IRAS proposal to include state consumer advocates in the list of those allowed to access confidential information in the proposed new Large Load Registry. PDF p. 2
ER26-3515-000 · 2026-09-03
Thus, there should be no concern about data protection standards for state commissions with access to the registry. PDF p. 6
ER26-3515-000 · 2026-09-03
One request is appropriately resolved within the Section 205 standard of review: PJM’s filed tariff and registry already collect each Large Load’s Peak Shaving Adjustment value under a qualifying state program, yet the filing does not specify how verified PSA megawatts reduce a Large Load’s IRAS obligation. PDF p. 4
ER26-3515-000 · 2026-09-03
’s (“PJM”) Interim Resource Adequacy Service (“IRAS”) and Large Load Registry to Address System Reliability1 proposal should be rejected because it is unjust, unreasonable, and unduly discriminatory. PDF p. 1
ER26-3515-000 · 2026-09-03
42 36 Constellation does not object on jurisdictional (or other) grounds to the portion of PJM’s Proposal that would establish a Large Load Registry. PDF p. 9
ER26-3515-000 · 2026-09-03
SMECO respectfully requests that the Commission direct PJM to (i) file the Manual provisions implementing the Large Load Registry’s data formats, one-mile-site methodology, and confidentiality safeguards for review before -- not after -- the Large Load Registry becomes effective; (ii) clarify the scope of an Electric Distributor’s potential liability for registry information sourced from LSEs or Large Loads; and (iii) identify a mechanism for Electric Distributors to recover the reasonable costs of Large Load Registry compliance. PDF p. 13
ER26-3515-000 · 2026-09-03
”31 FirstEnergy does not object to many of these criteria, but notes that the criteria should not be finalized until the pro forma agreement and “registry” that are contemplated in the Order to Show Cause are finalized. PDF p. 12
ER26-3515-000 · 2026-09-03
To support IRAS, PJM is also proposing in the IRAS Proposal new definitions for Large Load, New Large Load, and Eligible New Large Load; the creation of a Large Load Registry; and the exclusion of New Large Loads from the Variable Resource Requirement (“VRR”) curve starting in the 2029/2030 Delivery Year. PDF p. 1
ER26-3515-000 · 2026-09-03
Its recommendations can be summarized as follows: First, existing large loads should be excluded from the Large Load Registry. PDF p. 4
ER26-3515-000 · 2026-09-03
Accordingly, for the reasons that follow, the Commission should accept the Large Load Registry (the only legally defensible part of PJM’s proposal), while rejecting IRAS and directing PJM onto a different, more sustainable path that will actually improve resource adequacy in the region to the benefit of all stakeholders, including retail customers. PDF p. 3
ER26-3515-000 · 2026-09-03
ODEC also agrees that the Large Load Registry is generally consistent with the Commission’s June 2026 Order to Show Cause regarding large loads, where the Commission determined that PJM’s Tariff appeared to be unjust and unreasonable absent provisions “that would require PJM and the Transmission Owners to publicly post and regularly update data that details (1) aggregate amounts of proposed large load additions in PJM’s footprint. PDF p. 3
ER26-3515-000 · 2026-09-03
The Commission should require PJM to distinguish between providing telemetry information as part of the Large Load Registry and establishing a PJM telemetry requirement for the operation and measurement of an IRAS reduction. PDF p. 27
ER26-3515-000 · 2026-09-04
OPSI SUPPORTS THE LARGE LOAD REGISTRY TO INFORM RETAIL CURTAILMENT AND COST ALLOCATION OPSI supports PJM’s proposed Large Load Registry because it will provide states and Electric Distributors with the information needed to design and administer retail curtailment and cost-allocation mechanisms for NLLs. PDF p. 7
ER26-3515-000 · 2026-09-04
PJM’S INCLUSION OF PEAK SHAVING ADJUSTMENTS IN THE LARGE LOAD REGISTRY IS LAUDABLE, BUT TO ALIGN INCENTIVES, THE MECHANISM SHOULD ALSO BE CREDITED IN THE CALCULATION OF IRAS-ELIGIBLE LOAD AMOUNTS As currently drafted, Peak Shaving Adjustment values are to be separately tracked in the Large Load Registry for each New Large Load16 yet play no role in the calculation of the Eligible New Large Load Amount as written,17 with the potential effect that a Peak Shaving Adjustment does not reduce a Large Load's exposure to IRAS curtailment. PDF p. 23
ER26-3515-000 · 2026-09-08
1 Among other things, IRAS would identify NLLs that have not brought capacity to meet their needs in an NLL registry and permit PJM to send a wholesale curtailment signal, equivalent to the NLL quantity that does not have associated capacity, prior to entering into pre-emergency procedures. PDF p. 1
ER26-3515-000 · 2026-09-11
CyrusOne would be a “New Large Load” within the meaning of the IRAS Filing with respect to qualifying load, and its facilities and expansion plans would be directly affected by the proposed Large Load and New Large Load definitions, the Large Load Registry, and the resulting IRAS curtailment framework. PDF p. 3
ER26-3515-000 · 2026-09-15
Existing large loads should be excluded from the Large Load Registry. PDF p. 1
ER26-3515-000 · 2026-09-18
To this end, the Board requests clarification on how PJM will use real-time demand from New Large Loads to inform curtailment directives, either through a more dynamic database in PJM’s proposed Large Load Registry, or through the development and maintenance of a different system entirely to assist in this process. PDF p. 3
ER26-3515-000 · 2026-10-08
The current Registry field set appropriately identifies the customer, EDC interconnection request, location, zone, business segment, 2026/27 and expected 2029/30 peak load, BYONC contract status, associated resource identifiers, BYONC MW, submitter contacts, and PJM's BYONC Status. PDF p. 2
ER26-3515-001 · 2026-11-09
7 never explains why state consumer advocate offices should be excluded from access to this information despite the demonstrated need for such access. PDF p. 9
Reliability and curtailment
ER26-3515-000 · 2026-09-03
However, PA PUC objects to the proposed, red- lined tariffed language at PJM’s Transmittal Appendix A at page 105 - X (Compensation for Providing Interim Resource Adequacy Service), which conflicts with averments in PJM’s Transmittal Letter at pages 106-107. PDF p. 2
ER26-3515-000 · 2026-09-03
7 The Commission should reject PJM’s treatment of IRAS as a compensable resource adequacy service, and instead direct PJM to modify the proposal to provide that new large loads that do not self-supply must take non-firm transmission service. PDF p. 2
ER26-3515-000 · 2026-09-03
I support approval of the Interim Resource Adequacy Service (IRAS), the Large Load Registry, and the Bring Your Own New Capacity (BYONC) provisions. PDF p. 1
ER26-3515-000 · 2026-09-03
Moreover, that additional 500 MW of curtailment from non-large load customers would be unnecessary, as an IRAS quantity equal to the New Large Load’s real-time load should be sufficient to address the reliability impacts of New Large Loads unsupported by new capacity. PDF p. 6
ER26-3515-000 · 2026-09-03
Third, curtailment-based Demand Resources should be eligible for BYONC without requiring generation or storage assets at the location. PDF p. 16
ER26-3515-000 · 2026-09-03
PJM does not explain why a modification of this consequence warrants less analytical support than its Tariff demands for a modification of the curve's shape in a quadrennial review, and the Commission would be shirking its regulatory responsibilities were it to accept such consequential changes without the important data such modeling and analysis would provide, especially in the face of meaningful evidence that the IRAS Proposal, if implemented, would exacerbate resource adequacy issues in PJM and result in increased costs overall. PDF p. 8
ER26-3515-000 · 2026-09-03
The Commission should accept PJM’s Interim Resource Adequacy Service and Large Load Registry with modifications to better achieve the IRAS’s objectives. PDF p. 3
ER26-3515-000 · 2026-09-03
They improve forecast accuracy, preserve technology neutrality, support resource adequacy, facilitate emerging state-level reliability initiatives, and ensure that customers funding reliability solutions receive comparable treatment regardless of whether those solutions are modeled as incremental supply or forecast reductions. PDF p. 1
ER26-3515-000 · 2026-09-03
The New Jersey Board of Public Utilities (“Board”) supports the Proposal with a limited protest, as it presents a largely workable solution to the region’s resource adequacy shortfall and appropriately incentivizes New Large Loads in the region to bring new capacity to the system. PDF p. 1
ER26-3515-000 · 2026-09-03
16 ERAS proposal created a framework for the expedited study of generator interconnection requests to address urgent, near-term resource adequacy and reliability needs. PDF p. 16
ER26-3515-000 · 2026-09-03
FERC should consider directing PJM to directly assign curtailment obligations and related costs to the New Large Loads driving the reliability concerns on the grid due to their failure to bring generating assets to the system to satisfy their capacity obligations. PDF p. 2
ER26-3515-000 · 2026-09-03
Should PJM fail to prioritize IRAS Actions, such as re-sequence them to occur just prior to the issuance of manual load shed under an EEA3, damage to retail ratepayers will already have been done. PDF p. 7
ER26-3515-000 · 2026-09-03
To protect reliability and prevent double counting, the offset should be subject to the following conditions: (a) Measurement and verification protocols consistent with the applicable qualifying state program; (b) Performance scoring that accounts for actual delivery during capacity shortage conditions; (c) Annual reconciliation of PSA values against observed load reductions; and (d) A prohibition on counting the same megawatt toward both a PSA offset and any other capacity resource obligation. PDF p. 6
ER26-3515-000 · 2026-09-03
We support refinements that ensure the program adequately rewards measurable peak-demand reductions, enables demand-side and distributed-energy resources to participate fully, and appropriately assigns curtailment risk to the loads associated with the identified resource adequacy concern. PDF p. 1
ER26-3515-000 · 2026-09-03
’s (“PJM”) Interim Resource Adequacy Service (“IRAS”) and Large Load Registry to Address System Reliability1 proposal should be rejected because it is unjust, unreasonable, and unduly discriminatory. PDF p. 1
ER26-3515-000 · 2026-09-03
PJM’s proposal also would discriminate among supply resources, by allowing New Large Loads to avoid potential curtailment only if they make arrangements with qualifying “new” capacity. PDF p. 2
ER26-3515-000 · 2026-09-03
Because that New Large Load is not consuming power to reduce, and because the Interim Resource Adequacy Service Action is directed to the Electric Distributor’s zone/area as a whole rather than to any specific load, the Electric Distributor’s only means of complying would be to curtail its core, non-Large-Load native customers. PDF p. 9
ER26-3515-000 · 2026-09-03
6 Calibrant respectfully asks for clarification that this insertion is not intended to prohibit Demand Resources that previously participated in the RPM from providing BYONC by installing reliable, steel-in-the-ground behind-the-meter storage or generation resources to enable additional demand flexibility. PDF p. 6
ER26-3515-000 · 2026-09-03
COMMENTS CEBA supports the broader policy objectives underlying PJM’s proposal: large customers that are driving significant load growth should be encouraged to support solutions that help solve regional resource adequacy challenges. PDF p. 2
ER26-3515-000 · 2026-09-03
5 another way, under IRAS, it should be unambiguous that only a New Large Load that choose to be curtailable in the interim in exchange for quicker interconnection to the grid is subject to curtailment under an IRAS Action directive. PDF p. 5
ER26-3515-000 · 2026-09-03
If cost-causation justifies putting the burden of the shortfall on New Large Loads through IRAS curtailment, existing generators who did not cause the shortfall should not simultaneously absorb the adverse market consequence through exclusion from serving that demand and resulting in suppressed prices, as discussed further below. PDF p. 7
ER26-3515-000 · 2026-09-03
PJM proposes that new large loads that contract with new capacity resources are not supposed to be exposed to the IRAS curtailment regime while new large loads that contract with otherwise identical existing capacity resources would be. PDF p. 3
ER26-3515-000 · 2026-09-03
I have been retained by the Electric Power Supply Association (“EPSA”) to submit this affidavit in support of its protest to PJM’s Interim Resource Adequacy Service (“IRAS”) proposal in Docket No. PDF p. 19
ER26-3515-000 · 2026-09-03
OELC supports the objective of maintaining resource adequacy and recognizes that new large loads should bear responsibility for the incremental resource-adequacy needs their additions create. PDF p. 1
ER26-3515-000 · 2026-09-03
”44 EKPC shares PJM’s concern about resource adequacy and the reliability challenges facing the PJM Region, supports measures that maintain resource adequacy, and recognizes the urgency of PJM’s reliability concerns. PDF p. 9
ER26-3515-000 · 2026-09-03
EXECUTIVE SUMMARY AEP recognizes that PJM faces a significant tightening of its Reliability Pricing Model (“RPM”) capacity market in recent years and subsequent resource adequacy shortfalls, and supports PJM taking action to mitigate the associated reliability risks. PDF p. 1
ER26-3515-000 · 2026-09-03
However, PJMICC is concerned that large retail customers who have contributed to resource adequacy for many years may be required to bear costs triggered by the rapid growth of new large- load customers. PDF p. 3
ER26-3515-000 · 2026-09-03
Doing so will insulate regular customers from load shed events that would not likely to occur but for the addition of power-hungry New Large Loads. PDF p. 7
ER26-3515-000 · 2026-09-03
Specifically, Google agrees that New Large Loads that do not bring sufficient new capacity to offset their expected demand should be subject to curtailment prior to other firm wholesale customers during tight system conditions, ensuring service to residential and other commercial customers remains reliable. PDF p. 1
ER26-3515-000 · 2026-09-03
, those that do not bring their own new capacity, should be the first to face curtailment if and when load shed is needed. PDF p. 1
ER26-3515-000 · 2026-09-03
5 responsible for capacity-related costs and transmission network service charges, the Commission should ensure that a load curtailment obligation is supported by an appropriate customer election, compensation mechanism, or corresponding adjustment in service rights and charges. PDF p. 5
ER26-3515-000 · 2026-09-03
PJM should provide clarification regarding how voltage stability impacts will be evaluated and which entity will be ultimately responsible for ensuring that Interim Resource Adequacy Service Action load reductions do not create adverse transmission or distribution system conditions. PDF p. 8
ER26-3515-000 · 2026-09-03
- 4 - the current rules are unjust and unreasonable, the Commission can, on the basis of the existing record, act without delay to direct PJM to immediately implement a remedy that would require LSEs hosting data centers that are interconnected without having obtained new capacity to require such data centers to contract with curtailment coordinators to provide curtailments to PJM. PDF p. 4
ER26-3515-000 · 2026-09-04
OPSI SUPPORTS CURTAILING NEW LARGE LOADS WITHOUT SUFFICIENT CAPACITY BEFORE PRE-EMERGENCY LOAD MANAGEMENT OPSI has supported the proposed curtailment priority throughout the Critical Issue Fast Path (“CIFP”) process this year. PDF p. 3
ER26-3515-000 · 2026-09-04
On the customer/aggregator side, there may be insufficient information available to check eligibility against a longer lookback: a site’s residents, owners, and/or operators may have no recollection or knowledge of long-past DR participation, or may confuse participation in a utility DR program carrying no resource adequacy benefits with support of a wholesale capacity product. PDF p. 22
ER26-3515-000 · 2026-09-08
1 Among other things, IRAS would identify NLLs that have not brought capacity to meet their needs in an NLL registry and permit PJM to send a wholesale curtailment signal, equivalent to the NLL quantity that does not have associated capacity, prior to entering into pre-emergency procedures. PDF p. 1
ER26-3515-000 · 2026-09-11
CyrusOne would be a “New Large Load” within the meaning of the IRAS Filing with respect to qualifying load, and its facilities and expansion plans would be directly affected by the proposed Large Load and New Large Load definitions, the Large Load Registry, and the resulting IRAS curtailment framework. PDF p. 3
ER26-3515-000 · 2026-09-15
Load netted against on-site generation under BTMG should be measured in a similar manner for IRAS purposes, providing certainty to retail customers who have invested in resource adequacy through retail BTMG. PDF p. 3
ER26-3515-000 · 2026-09-18
- 8 - the scope of New Large Loads to data centers would be consistent with the purpose of IRAS because the data center loads that are driving the resource adequacy concerns would still be subject to BYONC or curtailment. PDF p. 8
ER26-3515-000 · 2026-09-18
To this end, the Board requests clarification on how PJM will use real-time demand from New Large Loads to inform curtailment directives, either through a more dynamic database in PJM’s proposed Large Load Registry, or through the development and maintenance of a different system entirely to assist in this process. PDF p. 3