EL25-49: the filed comments

Positions read for this site

Each is a plain summary of one filing, checked against its pages. Where a stance is given, it is what the filing asks FERC to do with the proposal.

Constellation challenges the July 2028 date

Constellation and PJM · EL25-49-000 · 2026-10-14

Constellation questioned the proposed July 2028 start for interim network service. PJM answered that administering interruptions required new automation, but said it expected to take requests from September 2027.

AMP identifies a missing class of behind-the-meter generation

American Municipal Power and PJM · EL25-49-000 · 2026-10-14

AMP asked that the new service also cover non-retail behind-the-meter generation. PJM agreed to revise the language. On a separate objection from Amtrak and industrial customers, PJM said its changes did not impose the netting restriction they feared.

Which part could be filed in August?

PJM and Constellation · EL25-49-002 · 2026-08-14

PJM sought an extension to align its co-location and large-load work. Constellation wanted full interim network-service terms on the original schedule. FERC kept the August partial filing while granting additional time for other requirements.

Other passages, matched by topic

These passages match a topic and a request or argument in the same sentence. A filing can quote another party. Read its page before attributing a position.

Connecting load and generation

PJM

EL25-49-000 · 2026-10-14

I am submitting this affidavit in support of PJM’s proposed revisions to the PJM Open Access Transmission Tariff (“Tariff”) filed August 17, 2026, to comply with the Federal Energy Regulatory Commission’s (“Commission”) directives in its June 18, 2026 order,1 including the directive to reconsider the proposed effective date for PJM to offer the new transmission services for Eligible Customers taking service on behalf of Co-Located Load and load with Behind the Meter Generation. PDF p. 11

US SENATOR

EL25-49-000 · 2025-02-19

3 The Commission should give careful consideration to proposed changes to regional interconnection processes in a technical conference to ensure they do not interfere with that critical rule, undermine open access, or derail projects currently in the interconnection queue that are needed for resource adequacy. PDF p. 2

UNION OF CONCERNED SCIENTISTS

EL25-49-000 · 2025-04-11

”2 UCS also supports the Indicated PJM Transmission Owners view that “consider all the arrangements being contemplated or requested as being interconnected with and synchronized 2 Show Cause Order para 4, citing PJM Guidance on Co-Located Load (March 22, 2024). PDF p. 3

Pennsylvania Public Utility Commission

EL25-49-000 · 2025-04-22

8 To date, PA PUC has not made any such determination regarding co-located load arrangements, and the determination would be adjudicated under the unique facts of each case. PDF p. 4

Antora Energy LLC

EL25-49-000 · 2025-04-23

The pathway a resource takes to interconnect to the system, whether via a supply study process that incorporates co-located load or through an Electric Distribution Company (“EDC”) or Transmission Owner (“TO”) process for interconnecting load alone, should not itself cause disparate rate treatment independent of the characteristics of the underlying load and generation facilities. PDF p. 5

Buckeye Power, Inc.

EL25-49-000 · 2025-04-23

Buckeye also supports the additional options PJM has proposed to facilitate front-of-the-meter co-location arrangements where the co-located load is Network Load and resource adequacy is maintained. PDF p. 3

Solar Energy Industries Association

EL25-49-000 · 2025-04-23

51 One assumption of this co-location interconnection study would be that the resources using this interconnection option would supply their entire output to the co-located load, and would not be exporting to the grid and therefore these arrangements should be exempt from traditional Network Upgrade triggers or full deliverability requirements. PDF p. 10

Electric Power Supply Association

EL25-49-000 · 2025-04-23

2 (citations omitted); “Consequently, the Commission should confirm that the existing PJM Tariff provisions regarding Network Service and Point-to-Point Service are sufficiently inclusive to cover the treatment of co-located load,” p. PDF p. 2

Ohio Federal Energy Advocate

EL25-49-000 · 2025-04-23

BYOG may provide a pathway in some states for new generation resources to support co-located load and also serve as PJM Capacity Resources. PDF p. 5

NORTHEASTERN REMC

EL25-49-000 · 2025-04-23

28 Given this reliance, NREMC co-located load should be designated as Network Load and be responsible for its share of transmission and ancillary service costs. PDF p. 7

PJM Industrial Customer Coalition and Industrial Energy Cons

EL25-49-000 · 2025-04-23

The Indicated TOs have not provided adequate justification to demonstrate why co-located load that is not present on the grid during relevant system peaks should be treated in a completely different manner than other load on the system that curtails or is otherwise not present on the grid during relevant system peaks. PDF p. 7

Consumers' Research

EL25-49-000 · 2025-04-23

, a new fossil-fuel-powered generator) and will also increase grid reliability overall (rather than decrease it), then FERC should consider policies that allow that new generation to move ahead in the interconnection queue, in front of projects for non-dispatchable resources. PDF p. 4

Bloom Energy Corporation

EL25-49-000 · 2025-04-23

23 While each of PJM and the transmission owner may have different roles in the study, both would take the Energy Park as a whole into account for purposes of their studies, similar to the coordinated roles currently in place in the interconnection queue for generators. PDF p. 10

Data Center Coalition

EL25-49-000 · 2025-04-23

This would allow PJM, TOs, large load customers, and other interested parties to engage in a focused and facilitated dialogue aimed at expeditiously resolving the most contentious issues, including tariff clarity, network service classification, and the integration of co-located load into planning processes. PDF p. 8

Invenergy Renewables LLCInvenergy Thermal LLC

EL25-49-000 · 2025-04-23

Rather, it should seize this opportunity to articulate a new, proactive paradigm for jointly studying large-load interconnection requests as part of the generator interconnection queue, thereby ensuring that RTOs/ISOs engage in coordinated load, interconnection, and transmission planning that enhances resource adequacy and reliability, while efficiently deploying generation and allocating scarce transmission where it is most needed. PDF p. 2

BrightNight Power Marketing, LLC

EL25-49-000 · 2025-04-23

In the Show Cause Order, the Commission directed PJM and the PJM Transmissions to either explain why the existing PJM governing documents are just and reasonable and not unduly discriminatory or preferential without provisions specifically addressing co-located load arrangements or explain what changes would remedy the Commission’s concerns. PDF p. 2

Northern Virginia Electric Cooperative, Inc.

EL25-49-000 · 2025-04-23

Although there may be a variety of potential configurations, in the end the determination of whether co-located load or the supplier to such load should be required to obtain and pay for transmission service turns on whether the load and the generation serving it 18 Id. PDF p. 6

JOHNS HOPKINS UNIVERSITY

EL25-49-000 · 2025-04-23

If the Commission elects to direct changes to PJM’s existing tariff methodology for assigning transmission charges to co-located load, it should ensure that use-cases with similar electrical impacts pay comparable rates. PDF p. 5

Vistra Corp.

EL25-49-000 · 2025-04-23

at 13-14 (explaining that fully isolated behind-the-meter co-located load is ‘a new potential option’ for which “[t]ariff modifications would be needed based on the Commission’s November 1, 2024 Order in Docket No. PDF p. 10

Monitoring Analytics, LLC

EL25-49-000 · 2025-04-23

Applications for co-located load would be expected to increase substantially if the Commission were to allow co-located load. PDF p. 4

RMI

EL25-49-000 · 2025-04-24

In a black start eventuality, it stands to reason that the grid would be in distress and availing itself of its claim on the legacy gas generator; it follows that the benefits and the costs of black start service should accrue to Network Load, not the co-located load that would not be relying on any grid resources during the event. PDF p. 4

Center for Biological Diversity

EL25-49-000 · 2025-04-24

In particular, in their comments on the Order, the Indicated PJM Owners correctly explain that co-located load should be treated as load in front of the meter and subject to FERC and RTO rules. PDF p. 26

Clean Air Task Force

EL25-49-000 · 2025-04-25

Furthermore, until such generally applicable rules are created, FERC should not approve any waivers for interconnection service agreements. PDF p. 3

ROCKY MOUNTAIN INSTITUTE

EL25-49-000 · 2025-04-29

In a black start eventuality, it stands to reason that the grid would be in distress and availing itself of its claim on the legacy gas generator; it follows that the benefits and the costs of black start service should accrue to Network Load, not the co-located load that would not be relying on any grid resources during the event. PDF p. 4

Constellation Energy Generation, LLC

EL25-49-000 · 2025-12-05

The Commission Should Request Further Evidence in Other Regions The NOPR should solicit specific additional evidence of unjust and unreasonable interconnection service for large loads and/or undue discrimination against configuration disfavored by Transmission Owners to support the Commission’s required showing under section 206 of the FPA in each region or state, as it already has in PJM. PDF p. 14

Exelon CorporationThe FirstEnergy Transmission Companies

EL25-49-002 · 2026-01-16

No uncertainty exists and thus the allegation of uncertainty does not support finding the PJM Tariff unjust and unreasonable and fixing a new rate with new interim service and CD Service based upon net load of a co-located load customer. PDF p. 17

PJM Industrial Customer Coalition and Industrial Energy Cons

EL25-49-002 · 2026-01-20

To best effectuate the Commission’s attempt to introduce choice, flexibility, and clarity into the transmission and capacity planning process in PJM, the Commission should clarify that all load—including Co-Located Load, retail customers with BTMG, and retail customers without BTMG—must be provided access to the New Services. PDF p. 6

Eolian, L.P.Antora Energy LLC

EL25-49-002 · 2026-01-20

”15 We seek clarification that, as applied to an interconnection request by a Co-Located Load that includes energy storage components, this means that to the extent PJM performs study steps involving withdrawal assumptions from both the storage facility components and the co-located load components, these study steps must allow the interconnection customer to provide for limits to the injection and withdrawal rights for the generation and co-located load facilities reflecting the proposed integration of those facilities. PDF p. 6

Constellation Energy Generation, LLC

EL25-49-002 · 2026-01-20

First, consistent with existing rules for non-firm exports, a capacity resource should not be required to delist when it is serving Co-Located Load2 taking non-firm contract demand transmission service, so long as the capacity resource has no obligation to serve the Co-Located Load during a capacity emergency. PDF p. 1

Constellation Energy Generation, LLC

EL25-49-000 · 2026-02-02

44 And because the Commission has jurisdiction over the provision of such transmission service, it has the authority to regulate the type of transmission service taken by “an Eligible Customer taking transmission service on behalf of a Co-Located Load,” whether that service is Network Service (to which Exelon and FirstEnergy do not object) or Contract Demand services. PDF p. 10

Monitoring Analytics, LLC

EL25-49-000 · 2026-02-05

If, for example, the co-located load model were extended to all the nuclear plants in PJM, the impact on the PJM grid and markets would be extreme. PDF p. 5

Pennsylvania Office of Consumer Advocate

EL25-49-000 · 2026-02-19

”25 In evaluating PJM’s tariff revisions, FERC should ensure that PJM has clarified exactly how it interprets the definitions of BTMG and Co-Located Load, especially in relation to jurisdiction. PDF p. 6

PJM Interconnection, L.L.C.

EL25-49-000 · 2026-03-09

In the case of Co-located Load internal to the PJM system, that Co-Located Load would be, in the Requester’s view, not capacity backed. PDF p. 3

Invenergy Renewables LLCInvenergy Thermal LLC

EL25-49-000 · 2026-03-16

In addition, Invenergy seeks clarity on the following questions: (1) In the context of co-location arrangements, would a co-located generator qualify as an Eligible Customer on behalf of the co-located load? PDF p. 6

Enchanted Rock, LLC

EL25-49-000 · 2026-03-25

9 For these reasons, and the reasons set forth herein, Enchanted Rock respectfully requests that in any final order issued in the above-captioned proceedings, that the Commission 1) hold that PJM’s Proposed Interim NITS Limitation is prohibited, and 2) direct PJM to file revisions to its tariff to clarify that a Co-Located Load can be served by its Co-Located Generating Facility during the Interim Period, consistent with the applicable holdings and directives in the December 18 Order. PDF p. 3

Maryland Office of People's Counsel

EL25-49-000 · 2026-04-24

If the capacity of existing generation that shifts to serve new co-located data center load is added to the BRA, ratepayers would be saddled with enormous costs that should be assigned to the co-located load, in contravention of the Statement of Principles and the Ratepayer Protection Pledge. PDF p. 11

Cost allocation

Electric Power Supply AssociationPJM Power Providers GroupCalpine Corporation ,Cogentrix Energy Power Management, LLC ,Constellation Energy Generation, LLC ,LS Power Development, LLC ,

EL25-49-000 · 2025-04-22

The Commission should direct parties to this settlement process to identify an acceptable replacement rate that reasonably establishes the services, if any, used by co-located loads, and allocates any costs to such loads (or the generator serving them) consistent with cost causation principles. PDF p. 2

Pennsylvania Public Utility Commission

EL25-49-000 · 2025-04-22

15 Because of the lumpiness of the load, and the size of network upgrades that are driven mostly by these singular load additions, the Commission and PJM should revisit the potential direct allocation of transmission network upgrade costs to very large loads. PDF p. 8

Delaware Public Service Commission

EL25-49-000 · 2025-04-23

COMMENTS In response to the Commission’s inquiry, the DEPSC expresses support for the Comments of OPSI in this proceeding as it relates to resource adequacy, transparency, consumer protection, cost allocation, and jurisdiction. PDF p. 5

Buckeye Power, Inc.

EL25-49-000 · 2025-04-23

”17 Buckeye agrees that forecasting and cost allocation issues associated with large loads are a significant concern and one that the Commission should address, regardless of whether that load is co-located with generation or not. PDF p. 10

Mainspring Energy

EL25-49-000 · 2025-04-23

In the attached comments, Mainspring: ●​ Supports PJM’s exploration of new flexibility frameworks, including Options 6 and 7;​ ●​ Recommends preserving the two existing BTMG classes (retail and non-retail) while establishing a new tariff-defined class for repurposed legacy generation (Option 3);​ ●​ Proposes specific tariff language to support this third class and improve transparency around cost allocation and interconnection study requirements;​ PDF p. 1

NORTHEASTERN REMC

EL25-49-000 · 2025-04-23

CONCLUSION For the reasons stated above, NREMC respectfully requests that the Commission find the current PJM Tariff is just, reasonable, and non-discriminatory or preferential as it already accommodates co-location arrangements through Network Service and Point to Point Service, which uphold equitable cost allocation for the transmission and grid services co-location arrangements benefit from. PDF p. 8

PJM Industrial Customer Coalition and Industrial Energy Cons

EL25-49-000 · 2025-04-23

The Indicated TOs give lip service to cost causation as the governing principle,26 but they explicitly promote a discriminatory construct in which reductions of system load would significantly favor customers curtailing load versus customers who offset their load by building or co-locating with generation. PDF p. 7

Bloom Energy Corporation

EL25-49-000 · 2025-04-23

15 PJM proffers that “very large loads like data centers” (another undefined term) perhaps should be treated differently based on cost causation principles,16 yet provides nothing more. PDF p. 8

Data Center Coalition

EL25-49-000 · 2025-04-23

● Ensuring Grid Reliability and Fair Cost Allocation: Co-location should be subject to appropriate grid impact assessments and planning oversight. PDF p. 4

Vistra Corp.

EL25-49-000 · 2025-04-23

This cost allocation would be consistent with the cost causation principle because such upgrades are designed to facilitate the co-location arrangement. PDF p. 25

Center for Biological Diversity

EL25-49-000 · 2025-04-24

Appropriate Oversight Of Cost Allocation Formulas Is Necessary To Protect Against Ratepayers Being Improperly Charged For Infrastructure Costs to Support These Facilities 3. PDF p. 2

EXUS RENEWABLES NORTH AMERICA

EL25-49-000 · 2025-05-15

existing grid and customer base would not be adversely impacted by the large load addition because the large load would not be causing improper cost shifts or facilitating the removal of any existing generation capacity from participating in the PJM-administered markets. PDF p. 3

US SENATOR

EL25-49-000 · 2025-11-25

FERC can and should investigate existing methods for cost allocation to determine how much residential ratepayers are paying for transmission and, if necessary, require subsequent action to ensure data center owners and operators do not burden households with more than their fair share of power infrastructure costs. PDF p. 2

EARTHJUSTICE

EL25-49-002 · 2026-01-20

Furthermore, the Commission should direct PJM and its Transmission Owners to provide transparent reporting for major projects that explicitly compares incremental cost causation against pro-rata billing determinant recovery, ensuring the resulting allocation is not unjust and unreasonable, or unduly discriminatory or preferential. PDF p. 8

Pennsylvania Office of Consumer Advocate

EL25-49-000 · 2026-02-19

5 In addressing PJM’s BTMG rule, FERC should adhere to the jurisdictional limits expressed in the Order to preserve exclusive state retail authority and protect consumers from cost shifts, because doing so will improve the Order’s legal durability and effectuate its purpose. PDF p. 2

Invenergy Renewables LLCInvenergy Thermal LLC

EL25-49-000 · 2026-03-16

Synchronizing the generator interconnection and transmission study processes would therefore provide practical benefits to developers, who could more easily finance and bring projects online more quickly, and save ratepayers money. PDF p. 2

ALLIANCE TO SAVE ENERGY

EL25-49-000 · 2026-03-26

Summary of Position The Alliance to Save Energy supports clear, durable rules that enable responsible large-load integration while preserving reliability, cost causation, and affordability. PDF p. 2

EARTHJUSTICE

EL25-49-000 · 2026-04-24

The Commission should require PJM to clarify that hybrid co-located facilities can nominate their net withdrawal limitations for purposes of the Necessary Study Process to avoid excessive and unnecessary network upgrade costs for hybrid generators. PDF p. 22

Maryland Office of People's Counsel

EL25-49-000 · 2026-04-24

The Commission should therefore require PJM to clarify whether these co-location rules are intended to apply to co-location arrangements undertaken with existing baseload generation so the effect of these transmission services on ratepayers can be determined and, if so, how adverse impacts on existing (particularly residential) customers can be mitigated. PDF p. 3

Filing procedure

Talen Energy Corporation

EL25-49-000 · 2025-04-09

’S MOTION FOR CLARIFICATION AND REQUEST FOR EXPEDITED TREATMENT1 Talen Energy Corporation (“Talen”) urges the Commission to act as soon as possible to opine on the merits of Talen’s November 20, 2024 Request for Rehearing in Docket No. PDF p. 1

Exelon CorporationThe FirstEnergy Transmission Companies

EL25-49-002 · 2026-01-16

Conclusion Because neither the Commission nor Constellation have satisfied their burden under FPA section 206 and the Commission has not engaged in reasoned decision making in the 206 Order, the Commission should grant rehearing, revoke its directives to establish new transmission service offerings, and instead, take no action pursuant to section 206 and find that the existing PJM Tariff is just and reasonable. PDF p. 57

PJM Industrial Customer Coalition and Industrial Energy Cons

EL25-49-002 · 2026-01-20

Further, because these critical issues remain unclarified in the Order currently, and because an inadequate record was developed on the impact of the retail behind-the-meter generation (“BTMG”) rule changes and the shift to a “gross load” approach for transmission cost responsibility, the Industrials also respectfully submit the Request for Rehearing herein in the event that the Commission does not grant all of the requested clarifications herein. PDF p. 2

Constellation Energy Generation, LLC

EL25-49-000 · 2026-02-02

EL25-49-000 EL25-49-002 AD24-11-000 AD24-11-001 EL25-20-000 EL25-20-001 (Consolidated) MOTION FOR LEAVE AND ANSWER OF CONSTELLATION ENERGY GENERATION, LLC Constellation moves for leave and submits this answer1 in response to the rehearing request filed by the Indicated PJM Transmission Owners2 in the above-captioned dockets. PDF p. 1

Monitoring Analytics, LLC

EL25-49-000 · 2026-02-05

3 Request for Clarification or, in the Alternative, Rehearing of Constellation Energy Generation, LLC, Docket Nos. PDF p. 1

Individual No Affiliation

EL25-49-002 · 2026-02-09

) ER25-2296-002 ____________________________________ ) AD24-11-000 ANDREW HINZ’S REQUEST FOR REHEARING ON FEDERAL INTERCONNECTION TARIFFS FOR LARGE LOADS CO-LOCATED AT GENERATING FACILITIES The Federal Energy Regulatory Commission (FERC) December 18, 2025 Order in EL25- 49 Etal will cause unjust and unreasonable rates because: 1. PDF p. 1

Pennsylvania Office of Consumer Advocate

EL25-49-000 · 2026-02-19

) (Consolidated) ) MOTION FOR LEAVE TO ANSWER AND ANSWER OF THE PENNSYLVANIA OFFICE OF CONSUMER ADVOCATE The Pennsylvania Office of Consumer Advocate (PA OCA) moves for leave to answer (Motion) and submits this Answer1 in support of the PJM Industrial Customer Coalition and the Industrial Energy Consumers of America’s (collectively, ICC) Request for Clarification or Rehearing (ICC’s Request) filed on January 20, 2026, to the Commission’s December 18 Order issued in the above-captioned docket (Order). PDF p. 1

PJM Interconnection, L.L.C.

EL25-49-000 · 2026-03-09

, Request for Clarification or, in the Alternative, Rehearing of Constellation Energy Generation, LLC, Docket Nos. PDF p. 1

Constellation Energy Generation, LLC

EL25-49-000 · 2026-08-04

Transmission, LP, 127 FERC ¶ 61,162, at P 6 (2009) (finding good cause to accept an answer to a rehearing request because the answer “provides information that will assist [the Commission] in [its] decision-making process”). PDF p. 1

Vistra Corp.

EL25-49-000 · 2026-08-18

3 Because NOVEC’s pleading was filed after the statutory deadline for requests for rehearing, it must be denied as untimely. PDF p. 1

Registry access

Pennsylvania Office of Consumer Advocate

EL25-49-000 · 2026-02-19

) (Consolidated) ) MOTION FOR LEAVE TO ANSWER AND ANSWER OF THE PENNSYLVANIA OFFICE OF CONSUMER ADVOCATE The Pennsylvania Office of Consumer Advocate (PA OCA) moves for leave to answer (Motion) and submits this Answer1 in support of the PJM Industrial Customer Coalition and the Industrial Energy Consumers of America’s (collectively, ICC) Request for Clarification or Rehearing (ICC’s Request) filed on January 20, 2026, to the Commission’s December 18 Order issued in the above-captioned docket (Order). PDF p. 1

Reliability and curtailment

PJM

EL25-49-000 · 2026-10-14

Those rules would need to define when service is available, the transmission capability that supports it, the events that permit or require curtailment, the sequence and priority of curtailment, restoration criteria, customer notification, and the treatment of partial curtailments. PDF p. 12

US SENATOR

EL25-49-000 · 2025-02-19

3 The Commission should give careful consideration to proposed changes to regional interconnection processes in a technical conference to ensure they do not interfere with that critical rule, undermine open access, or derail projects currently in the interconnection queue that are needed for resource adequacy. PDF p. 2

Antora Energy LLC

EL25-49-000 · 2025-04-23

Co-location of highly flexible, low load factor thermal energy storage can allow better utilization of variable renewable energy resources that might otherwise be curtailed, without causing additional co-incident peak demand and without impacting the ability of that renewable energy project to support resource adequacy goals. PDF p. 5

Delaware Public Service Commission

EL25-49-000 · 2025-04-23

Further, it is unlikely that DR would fully meet any remaining resource adequacy gap, as the day- to-day operational activation of DR would significantly increase, likely causing DR capacity market participation to decline. PDF p. 4

Buckeye Power, Inc.

EL25-49-000 · 2025-04-23

Buckeye also supports the additional options PJM has proposed to facilitate front-of-the-meter co-location arrangements where the co-located load is Network Load and resource adequacy is maintained. PDF p. 3

Edison Electric Institute

EL25-49-000 · 2025-04-23

First and foremost, the Commission should strive to ensure that reliable system operations and resource adequacy are maintained and enhanced over the long term. PDF p. 7

Ohio Federal Energy Advocate

EL25-49-000 · 2025-04-23

Because of the wider range of impact, co-location arrangements that take existing generation off the system should be subject to robust analysis before they are allowed to proceed, including studying the impacts on the markets, grid reliability, and resource adequacy. PDF p. 4

Bloom Energy Corporation

EL25-49-000 · 2025-04-23

This approach would in turn creates an incentive for data centers to bring along primary generation resources that supply their needs on-site, ease resource adequacy concerns that have been highlighted by PJM, NERC and others. PDF p. 2

Data Center Coalition

EL25-49-000 · 2025-04-23

These modest improvements would help ensure that infrastructure decisions made at the local level are visible within broader planning discussions and appropriately reflected in resource adequacy and transmission assessments. PDF p. 12

Invenergy Renewables LLCInvenergy Thermal LLC

EL25-49-000 · 2025-04-23

Rather, it should seize this opportunity to articulate a new, proactive paradigm for jointly studying large-load interconnection requests as part of the generator interconnection queue, thereby ensuring that RTOs/ISOs engage in coordinated load, interconnection, and transmission planning that enhances resource adequacy and reliability, while efficiently deploying generation and allocating scarce transmission where it is most needed. PDF p. 2

JOHNS HOPKINS UNIVERSITY

EL25-49-000 · 2025-04-23

While existing rules also allow utilities to ensure that new loads are connected in an orderly manner and that new service is only allowed to commence once transmission needs have been addressed, any accelerated co-location process must address what happens if a co-location request would precipitate a resource adequacy or affordability crisis. PDF p. 4

Business Council for Sustainable Energy

EL25-49-000 · 2025-04-23

3 BCSE supports FERC taking action as soon as is practicable to address the issues related to the co-location of large loads and encourages FERC and PJM to consider the specific issues in this context of energy reliability, resource adequacy, implications for energy costs, as well as infrastructure and transmission planning. PDF p. 2

Center for Biological Diversity

EL25-49-000 · 2025-04-24

Moreover, if engaging in demand response or power curtailment forces a data center to invest in more back-up generation, utilities and public utilities commissions (“PUCs”) should require that data centers prioritize on-site battery storage in conjunction with renewable energy, such as solar and wind, as well as investments in energy efficiency measures. PDF p. 17

Exelon CorporationThe FirstEnergy Transmission Companies

EL25-49-002 · 2026-01-16

The 206 Order also fails at the second step of FPA section 206 because the proposed replacement rate is not just and reasonable, would grant an undue preferential rate for co-located loads, and would exacerbate the resource adequacy, reliability constraints, and affordability concerns in PJM—all contrary to the FPA. PDF p. 34

PJM Industrial Customer Coalition and Industrial Energy Cons

EL25-49-002 · 2026-01-20

To avoid these results, the Commission should clarify that either (1) cogeneration QFs are exempt from the “gross load” approach mandated under the Order; or (2) PJM must include a reasonable “Back-up Power” transmission option that retail BTMG customers, including QFs, can purchase 17 The pending resource adequacy crisis in PJM has gained significant attention in recent months, at FERC and elsewhere. PDF p. 12

EARTHJUSTICE

EL25-49-002 · 2026-01-20

, Load Adjustment Request Implementation, PJM Resource Adequacy Planning Department (July 1, 2025; revised Aug. PDF p. 5

Constellation Energy Generation, LLC

EL25-49-002 · 2026-01-20

In that scenario, the capacity resource remains available to serve the grid when needed for resource adequacy; forcing the capacity resource nevertheless to delist would needlessly remove available capacity from serving the grid. PDF p. 1

Pennsylvania Office of Consumer Advocate

EL25-49-000 · 2026-02-19

Throughout this proceeding, the Commission should continue its vital focus on addressing new data center large load configurations that shift costs and create transmission and resource adequacy planning problems. PDF p. 3

PJM Interconnection, L.L.C.

EL25-49-000 · 2026-03-09

22 Otherwise, a resource’s commitment to provide capacity would not actually support or correlate with the resource adequacy needs of the PJM Region throughout the Delivery Year. PDF p. 6

Enchanted Rock, LLC

EL25-49-000 · 2026-03-25

As noted by the Data Center Coalition (“DCC”) in their answer to PJM’s February 23 Compliance Filing, the DCC stated that the Proposed Interim NITS Limitation “is unworkable because curtailment should limit use of the grid, not prevent the customer from using the co- located resource it supplied, which supports Interim NITS in the first place. PDF p. 9

ALLIANCE TO SAVE ENERGY

EL25-49-000 · 2026-03-26

The Alliance to Save Energy therefore recommends that PJM’s final tariff framework explicitly incorporate verifiable energy efficiency and demand flexibility into the conditions for favorable treatment. PDF p. 3

EARTHJUSTICE

EL25-49-000 · 2026-04-24

As explained below, to avoid such risks, the Commission should (1) accept PJM’s proposed operational penalties; (2) require PJM to clarify how and when curtailment directives will be enforced and how violations will be communicated to the public; (3) decline to require that PJM rush the implementation of protection mechanisms for its new non-firm transmission services; and (4) require PJM to make its co-located generator interconnection studies and retail-BTMG rules consistent with the Commission’s Order on the Show Cause Proceeding and Order No. PDF p. 2

Constellation Energy Generation, LLC

EL25-49-000 · 2026-09-08

PJM May Not Condition the Availability of Interim NITS on Resource Adequacy Considerations Constellation is concerned that PJM’s proposed tariff revisions will allow for anticipated resource adequacy concerns to form a basis for denying or limiting Interim NITS requests. PDF p. 8

Retail and wholesale authority

Northern Virginia Electric Cooperative, Inc.

EL25-49-000 · 2025-04-23

NOVEC respectfully requests that the Commission take care not to intrude on matters of state jurisdiction in the event that, notwithstanding these comments to the contrary, the Commission decides that some modification of PJM’s Tariff is warranted. PDF p. 8

Constellation Energy Generation, LLC

EL25-49-000 · 2025-12-05

at 12,370-71 (1996) (rejecting state commission’s argument that state jurisdiction should extend “to the ‘service’ of delivering electric energy to retail customers, which [the] state commission] would define to give it jurisdiction regardless of the nature and extent of the facilities used to make the delivery”). PDF p. 25

Exelon CorporationThe FirstEnergy Transmission Companies

EL25-49-002 · 2026-01-16

56 If one takes away the Commission’s intrusion into the terms of retail service (such as the issue of what distribution charges and responsibilities should be borne by the load, the terms of and charges for backup service to the load, and the terms by which the load might avoid paying for such service) nothing is left of CD Service. PDF p. 56

Constellation Energy Generation, LLC

EL25-49-002 · 2026-01-20

”16 The Commission should therefore clarify that state authority does not extend to the wholesale sale of energy by a generator to a retail supplier, even if the retail supplier then resells that energy to a load co-located with the generator. PDF p. 7

Constellation Energy Generation, LLC

EL25-49-000 · 2026-02-02

To conclude that the States’ authority over retail sales prohibits the Commission from regulating interstate transmission rates— as Exelon and FirstEnergy urge—would upend the FPA’s balance of federal and State jurisdiction. PDF p. 11